Smoke detectors in 2 unit rental

1.3K views 9 replies 9 participants last post by  azgard  
#1 ·
I'm bidding on a rewire for a house that will be turned into 2 units. The first floor is one unit and the second floor is the other. Each unit will have its own panel.

Does each unit get its own set of interconnected smokes? Or, do all of the smokes have to be on one circuit. I just figured that if there is a fire on one unit then the other unit should be notified somehow. This will be a rental. Thanks
 
#6 ·
sarness said:
Ask your ahj, mine says two separate systems.
My understanding is that if there is a firewall between the 2 units, then they count as separate structures and each unit will have its own interconnect system. If there isn't a fire rated wall separating the 2 units, then they are supposed to all be interconnected and powered from the house panel.