I tried to improve voltage drop in a 6 outlet circuit with no luck. The customer's complaint was that the 1500W heater, at the last outlet on the 15A circuit, was causing other stuff in the house to power down. Breaker was not tripping.
I put my 13A heat gun on the last outlet and indeed saw a 1.5V to 2.5V drop between each of the 6 outlets. The breaker output was 118.6V and the voltage at the last outlet was 108V
Since the 6 receptacles on this circuit were ancient and backstabbed, I thought I had a pretty good chance of improving the situation by pigtailing all 6 outlets.
I pigtailed them all but the voltage drop improvement was hardly noticeable.
Voltage drop calculators say I should see a drop of 1.97% at 13 amps for the 30 feet this circuit runs. However, I'm seeing more like 8.9%
Do the splices really drop this much voltage or am I missing something?
I put my 13A heat gun on the last outlet and indeed saw a 1.5V to 2.5V drop between each of the 6 outlets. The breaker output was 118.6V and the voltage at the last outlet was 108V
Since the 6 receptacles on this circuit were ancient and backstabbed, I thought I had a pretty good chance of improving the situation by pigtailing all 6 outlets.
I pigtailed them all but the voltage drop improvement was hardly noticeable.
Voltage drop calculators say I should see a drop of 1.97% at 13 amps for the 30 feet this circuit runs. However, I'm seeing more like 8.9%
Do the splices really drop this much voltage or am I missing something?