Sub panel in detached structure

15K views 33 replies 10 participants last post by  kolyan2k  
#1 ·
Is there something specific you need to do per NEC for installation of 100amp sub panel? I want to run
3-3-3-8 Cu (or 1-1-1-6 Al) THWN inside PVC underground and just install main lug panel.
 
#3 ·
One should favor 1,1,1,8 IMHO. I like Aluminum for my Hots, Copper for my bonding and grounding conductors.

The raceway :: 1 1/2" PVC schedule 40. I'd rather have a loose pull.

Distance -- might make me bump up the conductors -- but I assume that this is a nearby out-building.

It's still going to need a Ufer or other Grounding Electrode System as it is not an attached structure.

Ask This Old House showed just such an install a few years back. It's on Utube.
 
#4 ·
The 6 stroke rule applies here, so if you are going to have more than 6 circuits, use a main breaker.

If it's new you need to install a UFER (attach to the rebar). If it's existing you need to drive a ground rod, which would mean 2 of them. If there is metal pipe you need to bond it.

Never run copper conductors, that is just silly.
 
#8 ·
225.30 Number of supplies. The six rule is mandated to conform to circuits approved by 225.30 and 225.30 doesn't allow up to six disconnects for a separate building downstream of the service disconnecting means unless they meet the provisions of 225.30 (A) thru (E). (You might be able to wrangle (E) since it is kinda vague who decides what is proper documentation and operation).........
 
#5 ·
I see... It's a new structure 150ft away as I was told, but I think they already have the foundation done, so I am guessing UFER is not an option anymore and then I would just need to install 2 electrodes

Ive recently done a small shed with 40amp subpanel (bathroom and sauna), ran 8/3 UF, inspector didn't mention anything about the need for grounding rods
 
#7 ·
You need a main disconnect, not necessarily main ocpd though but it's allowed. That being said, a main breaker panel is usually your cheapest option. Run a separate ground from the house and wire it like a subpanel Ground and bond it like a main service, but tie them to the separate ground bus, not neutral.
 
#16 ·
Ma may not require the ufer or concrete encased electrode . Nc still does not enforce the concrete encased electrode- I wish they would.

You do need an electrode at the shed if you install a panel. You need 2- hots, neutral and a ground. I don't know why the inspector didn't make you put it in...
 
#25 ·
Owner doesn't care if run Cu or Al. He actually priced all materials himself and included Cu. I usually run UF inside the pipe for protection, just wasn't sure if there is anything else with outer insulation that would work. It will be a pain to get PVC pipe all the way to the house panel. UF works great because you can run it inside PVC underground and when you enter the house no pipe is needed anymore
 
#31 ·
338.12 (A) (2) Uses Not Permitted. ... Underground with or without a raceway [regarding SER cable]


However the stuff I have seen has the individual conductors marked XHHW so it seems if the jacket was removed it would be OK.


I believe you should switch the bare aluminum ground to insulated or copper though because the water that always accumulates in the pipe would disintegrate bare aluminum after a while.
 
#32 ·
338.12 (A) (2) Uses Not Permitted. ... Underground with or without a raceway [regarding SER cable]


However the stuff I have seen has the individual conductors marked XHHW so it seems if the jacket was removed it would be OK.


I believe you should switch the bare aluminum ground to insulated or copper though because the water that always accumulates in the pipe would disintegrate bare aluminum after a while.

That happens to be the answer to the question he asked. The bare alum will go to powder in an underground ser wire pull if the teeniest hole in the sheath is present down there. And I don't think the insulation on SER is rated for fungus either. Sunlight and water- yes. Fungus amongus - no.