I just read the article about service conductors, feeders and branch circuits.
I'm guessing it's the tap conductor thing I'm having more problems with
I'm guessing it's the tap conductor thing I'm having more problems with
No, not at all. Take a feeder that is run from a panel to a trough and from there smaller ampacity conductors are spliced or tapped onto the larger feeder. These smaller conductors are not fused at their given ampacity but are protected by the larger feeder conductor. These wires must meet certain conditions, as mention in the graphs above, to be allowed to be protected at the larger ampacity.I read the definition but I guess it's hard for me to visualise what a tap conductor is.
"Basically a conductor is considered a tap conductor where it has overcurrent protection higher than its rated ampacity."
Does this mean for instance the rated ampacity of 14 AWG is 20 amps but if theconductor is protected by a 30 amp fuse or breaker it becomes a tap conductor?