Teck 90 in US Residential

5.8K views 31 replies 12 participants last post by  99cents  
#1 · (Edited)
I worked with "CLX" cable when I was in the oil patch, which I think is same-same with Teck-90?

Anyhow, I'm bidding a job to feed an outdoor above ground hot tub. The feed from the inside the house panel goes to an in-grade pvc box, but the trench from there to the HT disco goes over-down-and around some retaining walls. Seems to me a CLX/Teck 90 cable is perfect for this application.

Too many bends in the run so I'm wanting to run Teck 90.

I emailed the inspector to get his/her thoughts on this install but have not heard back from them yet.
Anyone else use this cable for US resi applications?

155557


You can't see the retaining wall's but you can see the slope angle here. I'd rather not deal with pvc or ltfmc and pull boxes. (the SO cord seen is from a temp connection not installed by me ((#8 btw)) )

Any American folks here use this wiring method in resi job's?

155560


I also asked the inspector what he thought about surface mounting a length of conduit to sleeve the CLX feeding the HT from the edge of patio to HT . I've not heard back on that either. We'd rather not have to demo the mortared flagstone
 
#2 ·
I had never heard of this Tech90 cable until I found this site.
Looked it up and thought that is something I could use were I'm working at now.
Found out it is made by Beldan.
Checked our local distributor and got a don't know if it's available in the US.
Been a week or so and yet to hear back.
 
#7 ·
I've ran miles of it, mostly geothermal power plants but elsewhere too.

I've used both the power version (600V to 35KV) and the control version. The largest was 1250MCM, 15KV, about 5" in diameter. Lots of 18/2 shielded, about 1/2" in diameter.

Around here, it takes a while to get but if you plan well, it isn't a problem.

I've used it in hazardous locations, the explosion-proof fittings are $$$ though.
 
#14 ·
I don't see why you could not use C-L-X Type MC cable in a residential setting. It seems like it is available online and not that expensive if you consider the time savings during installation.
I have never actually used it but from what I can see the waterproof fittings are what seem to cost the most.
"Authorized for use on services, feeders and branch circuits for power, lighting, control and signaling circuits in accordance with Articles 330 and 725 of the NEC"
 
#28 ·
Phase tape is something any respectable electrician would avoid as much as possible. Conductors 4/0 and larger would be a better number. I just cant understand the reason for restricting wire size. 4/0 and smaller is not much of a challenge to get the colors you want. I'm mainly talking "new construction" where you should have enough time to order wire of choice.

In emergency repairs phase tape should be used and I would not discourage it. I just cant wrap my head around why they limit it to #4 or larger. Too hard to wrap the tape on anything smaller.