What do those transformer fans run on?

8.8K views 21 replies 13 participants last post by  Zog  
#1 ·
I've seen name plates for those 115,000 to 13,200v 50MVA transformer and the like that have quite a few 16" fans on the fins. The name plates show interesting things like "excited winding" and all that but nothing about auxiliary power for cooling fans.

I'm pretty sure the cooling fan gets power from the transformer itself, but what kind of motors do they use? voltage? hp? single or 3 ph?
 
#2 ·
All the ones I've worked on, both dry type and oil filled, actually had totally separate circuits for the cooling fans supplied from the substation service, so they weren't directly connected to the distribution transformer at all.

They may make transformers that have a built in winding to supply auxiliary power, I just haven't seen one yet.

On our larger oil cooled units the fans are 3 phase but we also have some 10MVA dry types that have a bunch of 480V single phase fans. All the motors are fractional horsepower, with the largest being 3/4HP if I remember right.

-John
 
#8 ·
Those things are huge.
Image


163 tons.
Holds 13,000 gallons, or two fuel tanker full of transformer oil.
A lot of big radiator fans
 
#9 ·
Neat, I love that chit. I've never seen a sprinkler system set up on an outdoor transformer. I wonder if that's actually fire protection or if it can be used as emergency cooling?

I don't know if you Googled it, but apparently the "excited winding" is just an archaic term for the primary winding. They call the secondary the "coupled winding." :huh:

-John
 
#10 ·
I'm not sure, but I think they need to worry more about emergency containment than cooling. 13,000 gallon is quite a bit of oil. If it leaked even half, talk about environmental disaster.
 
#18 ·
Indeed they do, but any transformer, after years of operation, contaminates the oil so badly it is downright nasty. And if it experiences internal arcing or burns out, the nastiness gets a lot worse.....Many years ago I got to open a failed pole-top transformer...the smell was horrible. To give you an idea, think moldy tuna, rank tennis shoes, stinky armpits, stinky foot cheese, dirty underwear, rotten eggs and burned copper...combined...and that's about 1/3 of how bad it really was. I literally lost my lunch. :sick:
 
#17 ·
Transformer Fans

The power to run these fans depends on your available station service. For example: If you have a 138 kV/13.8 kV transformer, you would place station service transformers on your 13.8 kV side. At that point, it's just like hooking up regular pole-top distribution transformers. If you need 120/240V, hook it up. If you need 120/208/240 Volts, hook it up that way. Your station service provides power for your substation, including the radiator fans. If the transformer says OA/FOA on the nameplate, use of the fans will give the transformer a higher kVA/mVA rating. Now's the time to check your fans, before the return of summer.