What size OCP are the rest of you putting on a water heater in a dewelling that has a total connected load of 3500w or 3380w @ 208?
You don't really have to jump right to the 150% maximum rating for sizing your OCP when you only need to go to 125% for a single continuous load.You are right it should be 150% and I think most of us are using that.
Problem I'm having is seeing a HW tank with only 3500 watts and assumed 220V since it also has a rating for 208V. That's about 16 amps and is within the range of a 20 amp breaker on #12 wire.You don't really have to jump right to the 150% maximum rating for sizing your OCP when you only need to go to 125% for a single continuous load.
This could possibly lead to a savings of some material costs on multiple installs, such as, through lower ratings for certain types of fuses for example.
Not necessarily in this case, but still good to keep in mind for future bids.
3380w/208vX125% =20.31A. Next standard size 25A.
3500w/208vX125% =21.03A. Next standard size 25A
This allows for a safe, compliant installation that is well below the 150% maximum OCP rating allowed in 422.11[E].
BTW, I have lost count of how many times I have seen electric water heaters wired with #12 connected to a 25A or even a 30A CB. Oy!
You can if you'd like to but it's not required. If the panel is not within sight and 25ft you can install a breaker lock at the panel.Do you install a disconnect at the HW tank where you are?
Unless it's within sight of the panel, I will normally put in a 4SQ box with a 30A/DP toggle switch and RS cover. It also makes it easier for me later as I sometimes get calls to service the units.Do you install a disconnect at the HW tank where you are?
Micro, I don’t see a problem with how you’re doing it, especially since in this case that .3A is virtually nothing, but as usual, the code seems less than homogenous about this.I believe the OP is referring to a standard 4500 watt water heater.
The same unit operated at 208 volts will consume 3380 watts, and draw 16.25 amps. 16.25 X 1.25 = 20.3. According to 220.5 (B), you're allowed to drop the fraction if it's less than 0.5 In this case I use a 20 amp breaker and #12's.
I was called on this once by a highly respected inspector, and had to provide code references, but I think he already knew the answer, and was just testing me.
They have nothing to fail you on as long as it is not 12 gauge on a 30 amp breaker.And down here you will be going back to that job and replacing that 30a with a 25a before you would pass the final.
The OP said 3500w @ 208v....I believe the OP is referring to a standard 4500 watt water heater.
That is correct. I don't see how the wattage can be different for the same 208 voltage.The OP also said 3380. This is the wattage of a standard 4500 watt 240 volt element operated at 208 volts.
Rob